06-08-2011 10:30 AM
Hi everybody,
is it possible to use the embedded data logger in some kind of hardware triggered acquisition?
The PLC has to run at 2kHz with an inline model, but the data logger shall only log channel data upon rising edges of a digital line acquired by a DAQ card. The frequency of this signal will be somewhere between 0Hz-33Hz.
I'm thinking about making the Embedded Data Logger to be an ansynchronous device and trigger the TimedLoop by e.g. a RTSI line, but maybe there is an easier solution?
Cheers,
Swen
Solved! Go to Solution.
06-08-2011 10:57 AM
Hi Swen,
Assuming NI VeriStand 2010...To use the built-in EDL custom device in this manner, you'll trigger off of a channel in your system definition. The most direct implementation is to include the trigger source in the system definition by means of built-in hardware support (DAQ in your case), and map the trigger source to the "Log Trigger". The "Log Trigger" channel is found in the "Commands" section of the EDL custom device. You won't see this section until you add a log file to the EDL. The EDL is open source. If you look at the code (Custom Devices\National Instruments\Embedded Data Logger\Embedded Data Logger - Engine - PharLap.llb\Embedded Data Logger RT Driver VI.vi) you'll see it's an Inline Custom Device but it dynamically launches an asynchronous processes for File IO. That design mitigates the jitter that would be induced by doing file IO inside the Primary Control Loop.
One concern I have is your trigger signal rate, but it would help to have more information about your requirements. Do you want to log a set of channel values only at the exact instant the DI line transitions? If that's the case, mapping "Log Trigger" to the DI line might not work depending on the tolerance of the sample time (e.g. 'sample all channel values one time within 500 us of the trigger'). More information would help.
Steve K
06-08-2011 11:32 AM - edited 06-08-2011 11:37 AM
Hi Steve,
mapping the DI line to the data logger trigger is an option, thanks for the hint.
I will check the requirements for the maximum time between occurence of trigger signal on hardware and acquiring the data by the logger.
Another thing is that logging shall only be done once upon a low->high transition. If I directly map the DAQ line to the trigger channel values will be recorded as long as the line state is high. I.e I will have to buffer the current line state into an user variable and check the current line state to the n-1 line state by a calculated channel (conditional). Then map this calculated channel to the logger trigger channel. In which order are these steps done? Will I get the result of a low->high transition during a single iteration of the PLC?
Cheers,
Swen
06-09-2011 11:58 AM
Hi Swen,
It order of execution depends on the controller's mode: parallel or low latency. You'll need to refer to Understanding the VeriStand Engine also.
Engine Step | Target in Parallel Mode | Target in Low Latency Mode |
---|---|---|
1. | Read HW inputs | Read HW inputs |
2. | Read asynchronous custom device FIFOs (N-1) | Read asynchronous custom device FIFOs (N-1) |
3. | Read Data From HW of inline HW custom devices | Read Data From HW of inline HW custom devices |
4. | Read from models | Read from Data Processing Loop (N-1) |
5. | Read from Data Processing Loop (N-1) | Process system mappings |
6. | Process system mappings | Execute Model of inline model custom devices |
7. | Execute Model of Inline Model custom devices | Process system mappings |
8. | Process system mappings | Execute generators |
9. | Execute generators | Process system mappings |
10. | Process system mappings | Write to models |
11. | Write to Data Processing loop | Wait for models to finish |
12. | Write to models | Read from models |
13. | Set HW outputs | Process system mappings |
14. | Write to HW of inline HW custom devices | Write to Data Processing Loop |
15. | Write asynchronous custom device FIFOs | Set HW outputs |
16. | Write to HW of inline HW custom devices | |
17. | Write to asynchronous device FIFOs |
An important note about NI VeriStand 2010: Data obtained in a previous step is not available to a subsequent step until a Process system mappings step has executed. If I understand your proposal correctly, then your system definition would contain the following:
DAQ digital input
One user channel for buffering
One calculated channel for comparing the buffer to the current data
System mappings for:
In parallel mode (default) I thinik things would run like this:
Iteration Y
So, to answer your question directly, you won't trigger the log from a DAQ read in the same iteration of the PCL. If everything's running on time, you'll have a one-tic delay because calculations happen in the DPL, but you'll still start logging within one dt of the PCL.
Regards,
Steve K
06-09-2011 12:17 PM
Another solution is to perform the calculation in an Inline Model custom device. This would get rid of the 1-tic delay.
Create a custom device input and an output channel. Map the DAQ input to the custom device input. Perform the calculation inside the custom device and write the result to the custom device output channel. Engine step 8 will map the result to the log trigger channel in the same iteration that read the hardware.
Steve K
06-09-2011 11:03 PM
06-10-2011 07:34 AM
Thanks Steve and Stephen,
I checked the requirements and the 1-cycle delay will be ok. No need to build a custom device.
Regards,