RTD-122 CJC configuration

Hi,

I need to set the attributes of a rtd-122 module with the extended fieldpoint command !D.  What should the value of the [positions field be if the targeted channel is the Cold Junction Compensation channel?
0 Kudos
Message 1 of 2
(2,893 Views)
CLiu,
 
The FP-TC-120 has a CJC channel and the positions field would be set to hex 0100 to set the range and/or attributes. The FP-RTD-122 is an RTD measurement module and does not have a CJC channel, so there is no valid value for the positions field to access CJC.

Regards,
Aaron
0 Kudos