11-01-2011 09:00 PM
Hi All,
I use cfP-2120 and a few Input/output other modules in which have cFP-DO-304.
The channel 0 of cFP – DO-304 module always set 1 when I power on for the field point.
Please help me soon.
11-02-2011 01:13 PM
Hi Nguyen,
I am a bit unsure what you are asking. We have a cFP-DO-403, and a cFP-DI-304, but not a cFP-DO-304. Which module are you asking about?
If it is the DO module, is the green LED for that channel light and green when you power on the FieldPoint? If so, this indicates that the channel is on and I would expect it to be high. Is your question how to set it back to low?
Thank you for your clarification.
~kgarrett
11-02-2011 09:37 PM
Hi,
I am sorry, The module is cfp-DO-403.
Yes, The green LED for that channel(Channel 0) light and green when you power on the FieldPoint, It allways put level hight, however, I have set low hight before and shutdown power for the system field point.
Thanks
Nguyen Van Hung
11-03-2011 10:49 AM
Hello Nguyen,
So, you set the channel to low (assign it a value of 0), save that configuration, then restart the FieldPoint and the value is high (1) instead of the low (0) value you set? How are you setting the value to low? Are you doing it in Measurement and Automation Explorer, under Devices and Interfaces? Or are you setting it with an executable that you are running on the cFieldPoint controller? Thanks!
~kgarrett
11-04-2011 06:44 AM
Hi kgarrett,
Thanks for your support.
I worked it ok.
I set again 0 at Power-up output value(boolean) in the channel configuration of Measurement and Automation Explorer and save it.
Best Regards,
Nguyen Van Hung
11-07-2011 10:04 AM
Great, Nguyen. I was going to make sure you had saved the setting in Measurement and Automation Explorer. It will only take effect through restart if you save the settings. Best of luck with the rest of your application!