Getting error while connecting OPC server & DSC module

Dear sir. i am getting the following error while connecting OPC server of SMAR Foundation Fieldbus module with the LabVIEW DSC module. The snapshot for the same is attached here. Kindly suggest the possible reasons for the same.Waiting for your reply. Thank you.screen shot.JPG

 

0 Kudos
Message 1 of 2
(2,068 Views)

This is a DCOM Security error. Typically this error occures when the proper DCOM permissions have not been applied to the server for Access and Launch. DCOM will tell the server if a request from a client appli8cation is coming from an allowed user. Likewise, a response from the server is validated int he same way. If DCOM informs either the server or client applications that a user is not authorized then the connection fails as denied.

 

Look at the documentation provided with the OPC server for recomdantions on DCOM Security settnigs.

Fred Loveless
Kepware Technologies
http://www.kepware.com
0 Kudos