Multifunction DAQ

cancel
Showing results for 
Search instead for 
Did you mean: 

Connecting a Veris Differential Pressure Sensor PXU to NI 6008

Solved!
Go to solution

I want to connect a Veris Industries Differential Pressure Transmitter Model PXULX05S to a National Instrument NI-6008.  I’m not sure of the wiring setup from the PXU to the NI-6008.

It is a 3 wire configuration.  Measurement type voltage 0-10v raw.  The scaled value will be 0-10 in. w.c.  I have a 24vdc power supply connected to the PXU unit.

How should I connect from the PXU to the NI 6008?

Thanks,

 

0 Kudos
Message 1 of 5
(3,285 Views)

Can you post the link to the manual for this device? Also is this a bridge based transducer? 

Carl W.
Applications Engineering
National Instruments
0 Kudos
Message 2 of 5
(3,271 Views)

Thank you for your response.

The sensor uses a ceramic capacitive pressure transducer with a frequency output.

I have attached a installation guide.

0 Kudos
Message 3 of 5
(3,259 Views)
Solution
Accepted by topic author Bigblue239

It looks like in Voltage mode you would hook up the out to an analog input channel on the 6008. Then the com to a ground on the 6008. The power comes from a power supply and make sure you are including this in your ground as the document lays out.

Carl W.
Applications Engineering
National Instruments
Message 4 of 5
(3,235 Views)

Thanks for the help.

0 Kudos
Message 5 of 5
(3,226 Views)