Hello there!

I am using a PCI-6110 DAQ and the purpose is to synchronize a DO with some AO.something like this:

lovlex123_0-1714635745652.png

 

Now, im using AO/StartTrigger to trigger a DO,however,this works fine on PXIe-6341(another card for test),but unable to work on PCI-6110

there is an error -200077 and it asks me to change sampTimingType from SampTime to OnDemand,obvious there is no such thing in DAQmx Timing VI.

Finally I choose to use a Timing Node to set sampTimingType as OnDemand, and a new error -200452 come.

 

Is there a way to solve this problem?

Here I post a example VI :

0 Kudos
Message 1 of 4
(124 Views)

By the way,this VI would run on a LV2012 computer ,so some newer function may not work.

0 Kudos
Message 2 of 4
(120 Views)
Solution
Accepted by topic author lovlex123

PXIe-6341 is an X Series DAQ. It supports digital waveform.

PCI-6110 is an S Series DAQ. It does not support digital waveform and hence does not support sample clock timing and triggering for DIO. Some S Series support correlated DIO which allows you to use the sample clock from AI or AO, but PCI-6110 is not one of them.

ZYOng_0-1714653179938.png

 

Reference: National Instruments PCI-6110 Manual

-------------------------------------------------------