Hi,
I'm looking to log data and compare against alarm levels at numerous controllers and send this data back to a server over the LAN. My experience with Touch Panels is limited. Does anyone know if touch panels are a good solution as the controller or will there be any networking problems. Not sure on the limitations of Win CE
Thanks,
06-12-2009 07:04 AM
06-15-2009 03:30 AM
06-15-2009 04:30 AM
06-15-2009 06:17 AM
The TPC 2106 should work and does support the USB 6008. The only cavaet is that you will need to use DAQmx Base, which cannot multithread. So, you won't be able to run analog inputs and outputs simultaneously. What that means is that if you are only running analog input (any number of channels), you should be fine; but if you want to do digital i/o or analog ouput, then you will need to stop analog input, then start analog output, stop that and then start digital i/o. Hope that makes sense. So, you for your application, the TPC 2106 should be fine to use with the USB 6008 using a DAQmx base driver.
For networking, you have a choice of using shared variables or TCP/IP communication; both communication methods are supported on the TPC 2106.
06-15-2009 06:22 AM
Perfect answer Adnan. Just what I needed to know.
Thanks