Hi Al,
It is expected that CPU usage will be 100% if you have the default pause time of 0 ms. However, if you are correctly changing the pause time, you should see this value decrease accordingly.
The important thing to remember is that the configuration settings you use in MAX are not neccessarily the same as the settings in your LabVIEW project. It is possible that you were correctly changing the pause time in MAX (by following the instructions in my previous post and clicking "Apply"), but when you went to run your program the project settings were being downloaded to your controller, changing the pause time back to 0 ms.
To change the pause time in your LabVIEW project (LabVIEW 8.0 and later), right-click your FieldPoint target and select "Properties". Go to the "Bank and Network Module" tab, change the pause time, and click "OK". After this you need to deploy the settings to your target. Right-click your target in the project and select "Deploy". You should now be using the proper pause time that you set.
If this still doesn't work for you, please let us know and I will try to determine what is causing this behavior.